      Motor compressors (hereinafter referred to as compressors) can be classified
      into motor faults and mechanical faults (including crankshafts, connecting rods,
      pistons, valve plates, cylinder head gaskets, etc.). Mechanical failure often
      causes the motor to overload or even stall, which is one of the main causes of
      motor damage.

      The damage of the motor is mainly caused by damage (short circuit) and open
      circuit of the stator winding insulation layer. When the stator winding is
      damaged, it is difficult to be discovered in time, and eventually the winding
      may be burnt. After the windings are burnt, some phenomena or direct causes of
      burning are masked, making post-mortem analysis and cause investigation
      difficult. However, the operation of the motor is inseparable from the normal
      power input, reasonable motor load, good heat dissipation and protection of the
      winding enameled wire insulation. Starting from these aspects, it is not
      difficult to find that the causes of winding burnout are as follows: (1)
      abnormal load and stall; (2) winding short circuit caused by metal chips; (3)
      contactor problem; (4) power supply Phase loss and voltage anomalies; (5)
      insufficient cooling; (6) vacuuming with a compressor. In fact, motor damage
      caused by a combination of factors is more common.

      Abnormal load and stall

      The motor load includes the load required to compress the gas and the load
      required to overcome the mechanical friction. If the pressure ratio is too
      large, or the pressure difference is too large, the compression process will be
      more difficult; the frictional resistance caused by the lubrication failure will
      increase, and the motor stall in extreme cases will greatly increase the motor
      load. Lubrication failure and increased frictional resistance are the primary
      causes of load anomalies. Dilute the lubricating oil, the oil is overheated, the
      coking and deterioration of the lubricating oil, and the lack of oil will
      destroy the normal lubrication, resulting in failure of lubrication. The liquid
      is diluted to dilute the lubricating oil, which affects the formation of the
      normal oil film on the friction surface, and even washes away the original oil
      film, increasing friction and wear. Overheating of the compressor can cause the
      lubricating oil to become thinner or even coked at a high temperature, which
      affects the formation of a normal oil film. The system does not return oil well,
      the compressor is short of oil, and naturally it is impossible to maintain
      normal lubrication. The high-speed rotation of the crankshaft and the high-speed
      movement of the connecting rod piston, the friction surface without the oil film
      protection will rapidly heat up, and the local high temperature causes the
      lubricating oil to evaporate or coke rapidly, which makes the lubrication of the
      part more difficult, and can cause local severe wear in a few seconds.
      Lubrication failure, local wear, and crankshaft rotation require more torque.
      Low-power compressors (such as refrigerators, household air-conditioner
      compressors) due to the small torque of the motor, the phenomenon of blockage
      (motor can not rotate) often occurs after the failure of lubrication, and enters
      the "blocking-heat protection-blocking" infinite loop, the motor burns only Time
      problem. The high-power semi-hermetic compressor motor has a large torque, local
      wear will not cause blocking, and the motor power will increase with load within
      a certain range, causing more serious wear and even causing seizure (the piston
      is stuck in the cylinder). Inside), the connecting rod is broken and the like is
      severely damaged.

      The current at the time of stalling (blocking current) is approximately 4-8
      times the normal operating current. At the moment of motor start-up, the peak
      current can approach or reach the stall current. Since the heat release of the
      resistor is proportional to the square of the current, the current during
      startup and stalling causes the winding to heat up rapidly. Thermal protection
      protects the electrode during stalling, but generally does not respond quickly,
      and does not prevent winding temperature changes caused by frequent starts.
      Frequent start-ups and abnormal loads cause the windings to withstand high
      temperatures and reduce the insulation properties of the enameled wire.

      In addition, the load required for the compressed gas also increases as the
      compression ratio increases and the pressure difference increases. Therefore,
      the use of high-temperature compressors for low temperatures or the use of
      low-temperature compressors for high temperatures can affect motor load and heat
      dissipation, which is not suitable and will shorten electrode life.

      After the winding insulation performance is deteriorated, if there are other
      factors (such as metal scraps forming a conductive loop, acidic lubricating oil,
      etc.), it is easy to cause short circuit and damage.

      Short circuit caused by metal chips

      The metal chips trapped in the windings are the main culprit for the short
      circuit and low grounding insulation values. The normal vibration of the
      compressor during operation and the twisting of the winding by the
      electromagnetic force at each start-up will promote the relative motion and
      friction between the metal chips interposed between the windings and the winding
      enameled wire. Sharp edges and swarf can scratch the enameled wire insulation
      and cause a short circuit.

      Sources of metal shavings include copper pipe scraps left during
      construction, welding slag, internal wear of the compressor, and metal chips
      that fall off when parts are damaged (such as broken valves). For fully enclosed
      compressors (including fully enclosed scroll compressors), these metal chips or
      granules can fall on the windings. For semi-hermetic compressors, some particles
      will flow in the system with gases and lubricants, and eventually the magnets
      will accumulate in the windings; some metal chips (such as bearing wear and
      motor rotor and stator wear (broom) will) Drop directly on the windings. Short
      circuiting is only a matter of time after metal chips are accumulated in the
      windings.

      Special attention needs to be paid to the two-stage compressor. In the
      two-stage compressor, the return air and the normal return oil directly enter
      the first stage (low pressure stage) cylinder, and after compression, enter the
      motor cavity cooling winding through the medium pressure tube, and then enter
      the second stage like the ordinary single stage compressor. (High pressure
      cylinder). The return air has lubricating oil, which has made the compression
      process like thin ice. If there is liquid back, the valve of the first stage
      cylinder can be easily broken. The broken valve piece can enter the winding
      after passing through the intermediate pressure tube. Therefore, the two-stage
      compressor is more prone to motor short circuit caused by metal chips than the
      single-stage compressor.

      Unfortunate things often come together, and the problematic compressors often
      smell the burnt smell of the lubricant during the startup analysis. When the
      metal surface is severely worn, the temperature is high, and the lubricating oil
      starts to coke at 175oC or more. If there is more water in the system (the
      vacuum is not ideal, the lubricating oil and the refrigerant have a large water
      content, and the air enters after the negative pressure return pipe is broken),
      the lubricating oil may be acidic. Acidic oils can corrode copper tubes and
      winding insulation. On the one hand, it causes copper plating. On the other
      hand, this kind of acidic lubricating oil containing copper atoms has poor
      insulation properties, which provides conditions for winding short circuits.

      Contactor problems

      The contactor is one of the important components in the motor control
      circuit. The irrational selection can destroy the best compressor. It is
      extremely important to select the contactor correctly according to the load.

      Contactors must be able to withstand harsh conditions such as fast cycling,
      continuous overload and low voltage. They must have a large enough area to
      dissipate the heat generated by the load current, and the choice of contact
      material must be prevented from soldering at high currents such as startup or
      stall.

      For safety and reliability, the compressor contactor must disconnect the
      three-phase circuit at the same time. Copeland does not recommend the method of
      disconnecting the two-phase circuit.

      In the United States, Copeland approved contactors must meet the following
      four items:

      · The contactor must meet the work and test guidelines specified in ARI
      Standard 780-78 "Special Contactor Standards".

      · The manufacturer must ensure that the contactor closes at room temperature
      at 80% of the lowest nameplate voltage.

      • When using a single contactor, the contactor rated current must be greater
      than the motor nameplate current rating (RLA). At the same time, the contactor
      must be able to withstand the motor stall current.

      · If there are other loads downstream of the contactor, such as motor fans,
      etc., it must also be considered.

      • When two contactors are used, the split winding stall rating of each
      contactor must be equal to or greater than the compressor half winding stall
      rating.

      The rated current of the contactor must not be lower than the rated current
      on the compressor nameplate. Contactors with small or poor quality cannot
      withstand compressor start-up, high current surges during stalling and low
      voltage, and are prone to single-phase or multi-phase contact jitter, soldering
      or even falling off, causing motor damage.

      Contactors with contact jitter frequently start and stop the motor. Frequent
      starting of the motor, large starting current and heat, will aggravate the aging
      of the winding insulation. At each start-up, the magnetic torque causes the
      motor windings to move slightly and rub against each other. If there are other
      factors (such as metal shavings, poorly insulating lubricants, etc.), it is easy
      to cause a short circuit between the windings. Thermal protection systems are
      not designed to prevent this damage. In addition, the dithered contactor coil is
      susceptible to failure. If the contact coil is damaged, a single-phase condition
      is likely to occur.

      If the contactor is selected to be small, the contacts cannot withstand
      arcing and high temperatures due to frequent on-off cycles or unstable control
      loop voltages, which may be soldered or detached from the contact holder. The
      soldered contacts will create a permanent single phase condition that causes the
      overload protector to continuously cycle on and off.

      It is important to emphasize that after the contactor contacts are soldered,
      all controls that rely on the contactor to disconnect the compressor power
      circuit (such as high and low pressure control, oil pressure control, defrost
      control, etc.) will all fail, and the compressor will be unprotected.
      status.

      Therefore, when the motor is burned, it is an indispensable process to check
      the contactor. Contactors are an important cause of motor damage that is often
      forgotten.

      Power supply phase loss and voltage anomaly

      Unusual voltage and phase loss can easily destroy any motor. The power supply
      voltage variation range cannot exceed ±10% of the rated voltage. The voltage
      imbalance between the three phases cannot exceed 5%. High-power motors must be
      powered independently to prevent low voltages from starting and operating other
      high-power equipment on the same line. The motor power cord must be able to
      carry the rated current of the motor.

      If the compressor is running when a phase loss occurs, it will continue to
      run but will have a large load current. The motor windings will overheat quickly
      and the compressor will be thermally protected under normal conditions. When the
      motor winding is cooled to the set temperature, the contactor will close, but
      the compressor will not start up, there will be a stall, and enter the
      "blocking-heat protection-blocking" infinite loop.

      The difference between modern motor windings is very small, and the
      difference in phase currents during power supply three-phase balancing can be
      ignored. Ideally, the phase voltages are always equal, as long as a protector is
      connected to either phase to prevent damage from overcurrent. It is actually
      difficult to guarantee the balance of the phase voltage.

      The calculation method of the voltage imbalance percentage is the ratio of
      the maximum deviation between the phase voltage and the average value of the
      three-phase voltage and the average value of the three-phase voltage. For
      example, the nominal 380V three-phase power supply, the voltage measured at the
      compressor terminal is 380V, 366V, respectively. 400V. The average value of the
      three-phase voltage can be calculated as 382V, and the maximum deviation is 20V,
      so the voltage imbalance percentage is 5.2%.

      As a result of the voltage imbalance, the load current imbalance during
      normal operation is 4-10 times the number of voltage imbalances. In the previous
      example, a 5.2% unbalanced voltage could cause a 50% current imbalance.

      The National Electrical Manufacturers Association (NEMA) Motor and Generator
      Standards publication states that the percentage of phase winding temperature
      rise due to unbalanced voltage is approximately twice the square of the voltage
      imbalance percentage. In the previous example, the voltage unbalance point is
      5.2, and the percentage of winding temperature increase is 54%. The result is
      that one phase winding is overheated and the other two windings are normal.

      A survey completed by U.L. (Underwriters Laboratories, USA) showed that 43%
      of power companies allowed 3% voltage imbalance, and another 30% of power
      companies allowed 5% voltage imbalance.

      Insufficient cooling

      Compressors with higher power are generally of the return air cooling type.
      The lower the evaporation temperature, the smaller the system mass flow tends to
      be. When the evaporation temperature is very low (more than the manufacturer's
      specifications), the flow is not enough to cool the motor and the motor will run
      at a higher temperature. Air-cooled compressors (generally not exceeding 10 HP)
      have little dependence on return air, but have clear requirements for compressor
      ambient temperature and cooling air volume.

      A large amount of refrigerant leakage will also cause a reduction in the mass
      flow of the system, and the cooling of the motor will also be affected. Some
      unattended cold storages, etc., often have to wait until the cooling effect is
      very poor, only to find a large amount of refrigerant leakage.

      Frequent protection occurs when the motor overheats. Some users do not go
      deeper to check the cause and even short-circuit the thermal protector, which is
      very bad. After a while, the motor will burn out.

      The compressor has a range of safe operating conditions. The main
      consideration for safety conditions is the load and cooling of the compressor
      and motor. Due to the different prices of compressors in different temperature
      zones, it has been common to use compressors in the domestic refrigeration
      industry in the past. With the growth of professional knowledge and the
      improvement of economic conditions, the situation has improved
      significantly.

      Vacuuming with a compressor

      Open refrigeration compressors have been forgotten, but there are still some
      on-site construction workers in the refrigeration industry who have retained the
      habit of using the compressor to pump vacuum. This is very dangerous.

      Air acts as an insulating medium. After the vacuum is applied to the sealed
      container, the discharge phenomenon between the electrodes inside is likely to
      occur. Therefore, as the degree of vacuum in the compressor casing is deepened,
      the insulating medium is lost between the exposed terminals in the casing or
      between the windings with minute damage of the insulating layer. Once energized,
      the motor may be short-circuited in an instant. If the housing leaks, it may
      also cause electric shock.

      Therefore, it is forbidden to use the compressor to evacuate, and when the
      system and the compressor are in a vacuum state (the refrigerant has not been
      added after the vacuum is exhausted), it is strictly forbidden to energize the
      compressor.

      Summary

      After the motor is burnt, the phenomenon of winding damage is covered, which
      causes certain difficulties for fault analysis. However, the root cause of
      damage to the compressor motor does not disappear. Abnormal load or even stall
      caused by poor lubrication or failure, insufficient heat dissipation, will
      shorten the life of the winding; the inclusion of metal chips in the winding
      provides a benefit for the short circuit; contactor welding will make the
      protection of the compressor impossible; An abnormality in the power supply on
      which the motor is running will fundamentally destroy any motor; vacuuming the
      compressor may cause the internal terminal to discharge.

      Unfortunately, the above disadvantages can also trigger each other: abnormal
      load and large current during stalling may lead to contactor soldering; single
      contact arcing or even soldering will cause phase imbalance or single phase;
      phase imbalance will cause Heat dissipation problem; insufficient heat
      dissipation can cause wear; wear will produce metal shavings…

      Therefore, proper installation and use of the compressor, as well as
      reasonable daily maintenance, can prevent the occurrence of unfavorable factors
      and is the fundamental way to avoid damage to the compressor motor.